NEC 220.83 help

Status
Not open for further replies.

mattvds

New User
Location
California, USA
Occupation
Home Owner
I'm installing solar batteries, which requires replacing my main panel and do load calculations based on NEC 220.83. I have a 240V 200A service, and no new loads are actually being added. But when the engineer for the solar company did the calculations, it showed my existing equipment was already well over 200A. So I'm trying to find out all the errors they made to unblock the permit.

I think I identified a few issues, and I wanted to run it by the knowledgable community here to make sure my understanding is correct, and ask for advice on how to handle some perhaps unique situations that I have.

1) I have 2 heat pump units with the following configuration: Both units have: 1 50A/2p breaker for condensor/evaporator and 1 30A/2p breaker for blower. The engineer calculated the total VA for A/C loads as sum of breakers * .75. This is much higher than the calculations obtained by looking at the LRA of the units and motor loads of the fans. Am I correct that I should use the actual loads versus basing it on the breaker size?

2) I have a 60A sub panel that contains mostly lighting loads, but also has an electric dryer load. They again used breaker size * .75 as the VA, instead of the nameplate VAs for the individual fixed appliances. I assume I can list the nameplate of the fixed appliance instead of the subpanel in the load calc? If so, how would I then show the "breaker size" for these?

3) Is there any modifers for multiple fixed appliances loads? 220.17 mentions applying a "demand factor". I have more than 4 non-cooking/non-hvac fixed appliances, so am I allowed to use the 75% multipler on the nameplate value on thoses? Likewise, we have 1 cooktop and 2 electric ovens, can I apply a demand factor to the nameplates of those, similiar to what is allowed with a range?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I would suggest you contact a local electrician, we are not allowed to assist DIY projects.
I am closing this thread, in accordance with the Forum Rules.
This site is designed for:
  • Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
* This NEC Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.
Reminder to all members, if you see a questionable post, feel free to report it by clicking "Report" at the bottom left corner of the post.
 
Status
Not open for further replies.
Top