Not open for further replies.

Greenboy

Member
Location
Seattle, WA
Are there any issues, code wise (building or electrical), to install open bottom switchboard directly to wood(Mezz level)? I am uncertain if the wood is fire rated.
 

big john

Senior Member
Location
Portland, ME
Also, you'll run afoul of 408.17:
Location Relative to Easily Ignitible Material.
Switchboards shall be placed so as to reduce to a minimum the probability of communicating fire to adjacent combustible materials. Where installed over a combustible floor, suitable protection thereto shall be provided.
 