Recently went through NEC training (from the NFPA). For wire sizing, they give two options, one based on 125% of the full load, and one based on the conditions of use.
Is this correct, or are we supposed to use 125% and the temperature deration of conductors?
Example:
460V, 20HP motor, powered by a VFD. From the NEC table, this has an FLC of 27A, or 33.75A @125%
If using THHN, I would look at the 75 deg column since the VFD has 75 deg terminals. This yields #10AWG wire
Now, if I assume that this is in a 40degC environment, can I still use #10 THHN, or would I have to move to #8 THHN?
Is this correct, or are we supposed to use 125% and the temperature deration of conductors?
Example:
460V, 20HP motor, powered by a VFD. From the NEC table, this has an FLC of 27A, or 33.75A @125%
If using THHN, I would look at the 75 deg column since the VFD has 75 deg terminals. This yields #10AWG wire
Now, if I assume that this is in a 40degC environment, can I still use #10 THHN, or would I have to move to #8 THHN?