Q2. There is an on going practice among electrical contractors in my area to connect a short piece of 14 AWG wire to the 12 AWG in a receptacle box. The purpose of this is to facilitate the use of the push in connectors on the back 15A receptacles on a 20A circuit. When I ask how is this permitted? They cite the fact that the device is rated 15A and therefore this practice is allowed according to the branch-circuit tap rules. Is this true?
A2. No. The minimum size conductor for a 20A circuit is 14 AWG [310.5].
Would'nt this be allowed according to Table 210.24? For a 20A circuit rating, one can use 14 for a tap. Don't think 310.5 is a reference to this question, either.
A2. No. The minimum size conductor for a 20A circuit is 14 AWG [310.5].
Would'nt this be allowed according to Table 210.24? For a 20A circuit rating, one can use 14 for a tap. Don't think 310.5 is a reference to this question, either.