MC Cable Wiring

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
If separate neutrals are required and wiring a job in MC cable are you better off using a separate 12/2 for each receptacle circuit or a multiple neutral MC cable? I would think multiple neutral cable would save a lot on qty. of cable although.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If separate neutrals are required and wiring a job in MC cable are you better off using a separate 12/2 for each receptacle circuit or a multiple neutral MC cable? I would think multiple neutral cable would save a lot on qty. of cable although.

It also multiplies the number of joints you have to make in every box. In my opinion, 12/2 costs less to use, especially with labor in the equation.

t may even cost less per foot per circuit in materials alone.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Why instead of multiple neutral MC?

It's just easier to pull 12/2 instead of 12/4/4 and with 12/4/4 you have to somehow carry through the other 3 circuits which can lead to wiring errors. IMO it's just not worth it unless your plan is run the 12/4/4 to a big homerun box in the ceiling and then distribute from there. To run that out to a receptacle or switch box just isn't a good plan.
 

mstrlucky74

Senior Member
Location
NJ
It's just easier to pull 12/2 instead of 12/4/4 and with 12/4/4 you have to somehow carry through the other 3 circuits which can lead to wiring errors. IMO it's just not worth it unless your plan is run the 12/4/4 to a big homerun box in the ceiling and then distribute from there. To run that out to a receptacle or switch box just isn't a good plan.

Thank you.
 