Have been pondering and wondering something in my head and wanted make sure I am correct. If you have a standby generator with a manual transfer switch does the neutral have to get switched? Would like to know for both bonded generators and floating neutral generators.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The neutral/ground bond should be made either at both sources before the T/S, or at the load after the T/S, never both.

That's why it's tough, if not impossible, to mix bonded and un-bonded sources. One of them needs to be convertible.
 