jsieczko
Member
- Location
- Maplewood NJ
- Occupation
- Chief Architect
[We are going to try this again. I received my bachelors in electrical/computer engineering from Lehigh University in 1990 and am a member of Tau Beta Pi. I am not looking for "do it yourself advice" but have a question as a matter of intellectual and professional curiosity.]
I found it odd that my main panel had an 80 amp breaker feeding the sub-panel, but the sub-panel has a 70 amp breaker on the same feed. I would have thought that the breakers to be sized equivalently (80 -> 80). Is the step down a code requirement? Or did they just size the breaker for the anticipated load in the subpanel?
[The subpanel is grounded properly for a detached structure and I did a back of the envelop calculation for copper 3 THHN/THWN-2 wire with 2 current carrying conduits and got 85 amps, so 80 seems reasonable. The subpanel shows it was inspected.]
Joe
I found it odd that my main panel had an 80 amp breaker feeding the sub-panel, but the sub-panel has a 70 amp breaker on the same feed. I would have thought that the breakers to be sized equivalently (80 -> 80). Is the step down a code requirement? Or did they just size the breaker for the anticipated load in the subpanel?
[The subpanel is grounded properly for a detached structure and I did a back of the envelop calculation for copper 3 THHN/THWN-2 wire with 2 current carrying conduits and got 85 amps, so 80 seems reasonable. The subpanel shows it was inspected.]
Joe