Does a field installed main lugs have to have retaining clip? SER cable goes to the main lugs in panel. A second SER is also installed using the main lug kit. Does this kit need a retaining screw or clip?
 

hillbilly1

Senior Member
Location
Atlanta,Ga
Hold down clip not needed then, it is treated just like a breaker. If it was backfeeding the panel, then yes, it would need a mechanical means to hold it in.
 

kwired

Electron manager
Location
NE Nebraska
We are adding a plug in main lug kit. this is for a hotel we are rising up 4 floors. Each panel is fed in and out
Hold down clip not needed then, it is treated just like a breaker. If it was backfeeding the panel, then yes, it would need a mechanical means to hold it in.
If it is a plug on type "sub feed lug kit" then make sure your incoming feeder lands on the fixed main lugs and outgoing feeder lands on the plug on kit and you are fine.

If it is bolt on breaker type panel - it is already mechanically secured by the bolt on connection method.

If using commercial type panelboards instead of "loadcenters" why not order them with feed thru lugs, basically you will have lugs at both the top and bottom of the buses and either end can be the supply or the feed thru.
 