ewingc

New member
Location
Illinois
Are there guidelines within NEC/UL requiring circuit/conponent isolation to prevent low voltage wiring crossing high voltage (480)wiring within a enclosure. Example a stepdown transformer 115/277 to 24 volts within the same enclosure with the 480 main. The 24 volts controlling low voltage coils and relays.
 

tom baker

First Chief Moderator
Staff member
Re: low voltage wiring crossing 480 incoming power

Yes, but it depends on the what type of circuit the limited energy (low voltage) is. Separation is required for a class 2 or 3 limited energy circuit, but not a class 1 power limited circuit. Look at Art 725 to determine what type of limited energy circuit you have.
It may not be a problem.
 

jrdsg

Senior Member
Re: low voltage wiring crossing 480 incoming power

this is a common problem in the real world.

as consultants we have encountered numerous sites where there were separate parallel conduits run for high and low voltage [110 or 347 vs data or video] that emptied into common splice boxes or at the base of light standards.
 