Low Voltage sleeve requirements

Status
Not open for further replies.

mpwasco

Member
Location
oak Creek WI
Occupation
Project Manager
The question always comes up among the field workers....... Do you have to run an EMT sleeve through a wall for low voltage cables to pass through or can you just drill two holes on both sides of the drywall wall and fire caulk the hole after installation of the cable?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
For fire-rated penetrations, we have always done the sleeve, with fire caulk both within it and between it and the drywall.

For normal interior walls, not required.
 
Status
Not open for further replies.
Top