Does anybody know if it is required to have a lightning arrestor installed on a roof top mounted generator(diesel w/ day tank), roof is approx 100' high.
 

bphgravity

Senior Member
Location
Florida
Re: lightning arrestor

This is not a requirement of the NEC, however, further information can be found in the NFPA 780-1997, the Standard for the Installation of Lighting Protection Systems. :)
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: lightning arrestor

Are you asking for lightning protection or TVSS?

In my oppinion they should be both employed for the application you mentioned. Required by NEC not.
 