Lighting contactor question

Status
Not open for further replies.

tom_jlr

Member
I have a 3 pole, mechanically held contactor, with a 120v control coil (Eaton #ECC04C1A3A) controlling 277v lighting circuits.

Can I use 3 single pole lighting switches to control the contactor? Do I need to use 3-way and 4-way switches? Can I use a realy or low voltage switches to control the contactor?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Are you saying that the contactor has a single phase 120 volt coil? And are you suggesting that the coil be turned on or off using a set of three single pole switches? If the answers are both yes, then this won't work. How can you wire more than one single pole switch in such a way that operating any one will turn on and off the lights, regardless of the positions of the other two? It cannot be done. If you use two switches, then they need to be 3-ways. If you use any more than two switches, then the remainder have to be 4-ways.

Welcome to the forum.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Generally mechanically held contactors are switched by one SPDT switch, also called a 3-way switch. If you want to use more than one switch then you need to setup the system using only momentary contact switches. Otherwise the system will not work. With a relay accessory you can set them up to turn off and on with one single pole switch too.
 

dkidd

Senior Member
Location
here
Occupation
PE
All switches could be single pole double throw center off momentary. They could be wired in parallel.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If you used an accessory relay (like ASCO #47) you could use any standard combination of 3 and 4-way switches to switch the control circuit on and off.
 

iwire

Moderator
Staff member
Location
Massachusetts
Generally mechanically held contactors are switched by one SPDT switch, also called a 3-way switch. If you want to use more than one switch then you need to setup the system using only momentary contact switches. Otherwise the system will not work. With a relay accessory you can set them up to turn off and on with one single pole switch too.

Actually with a mechanically held contactor you can add as many momentary switches as you would like.

It is with electrically held contactors that switching gets trickier for multiple locations.
 

tom_jlr

Member
So, if I use single pole double throw center off momentary switches, I could use three or more of them with no issues, no extra wires?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So, if I use single pole double throw center off momentary switches, I could use three or more of them with no issues, no extra wires?

No issue just wire them all in parallel. You could add a momentary time clock too with this setup just wire that in parallel too.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Ahh when I read '3-way' I assumed you meant a standard 3-way set up when you were actually talking about SPDT momentary switches. :cool:

Actually I did mean a standard 3-way switch. If you're using one switch for on and off control a standard 3-way will work with a mechanically held contactor (at least the ASCO versions that we install).:grin:
 

iwire

Moderator
Staff member
Location
Massachusetts
Actually I did mean a standard 3-way switch. If you're using one switch for on and off control a standard 3-way will work with a mechanically held contactor (at least the ASCO versions that we install).:grin:

It can work but it makes the purchase of a mechanically held all but worthless (IMO) and you would be stuck with no more than one switch location.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It can work but it makes the purchase of a mechanically held all but worthless (IMO) and you would be stuck with no more than one switch location.

Worthless if multiple switching locations are needed. Pretty valuable if you need to turn on and off 12 circuits with one switch.
 

realolman

Senior Member
the less expensive electrically held one would work just as well, but the momentary switches with the mechanical one allow multiple parallel switch locations
 

iwire

Moderator
Staff member
Location
Massachusetts
Worthless if multiple switching locations are needed. Pretty valuable if you need to turn on and off 12 circuits with one switch.

I am not saying a contactor is a waste, just the added costs of mechanically held would be a waste. I would use an electrically held contactor for about 1/3 to 1/2 the cost of the mechanically held unit.

The last one I ordered was about 500 for electrically held and 900 for mechanically held.
 
Last edited: