Leviton box for splices

Status
Not open for further replies.

michalspike

Senior Member
Im doing Lutron radiora2 installation and they have lots of 0-10v modules. Can i use that Leviton 47605-28N box for splicing wires there?
Im not sure if this is code compliant to use it for splicing line voltage inside it/
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How would you separate the line and LV within the enclosure? I could see someone saying that the enclosure is not listed for the use that you've described. If the 0-10v is reclassified and installed as Class 1 then it can all be within the same enclosure.

ibcGetAttachment.jsp



http://www.leviton.com/OA_HTML/ProductDetail.jsp?partnumber=47605-28N&section=42390
 