Kitchen GFI's

Status
Not open for further replies.

mltech

Senior Member
Location
Ft. Lauderdale
Where does it state in the code that all Kitchen Receptacles must be gfi protected.
I have an inspector that said I could find it in 210.? I have a far wall in a kitchen that is over 10' from the sink and he is requesting that everything be Protected? I did it but would like
to have the code he is referring too.
Thanks
Mike
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Kitchen GFI's

210.8, note only commercial kitchens (other than dwellings 210.8(B)) require all receptacles to be GFCI.

Roger
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: Kitchen GFI's

2002 code requires all receptacles (120V 15 or 20A) in COMMERCIAL kitchens to be GFI.

210.8(B)(3) for other than dwelling units.

210.8(A)(6) for countertop outlets in a dwelling kitchen.

STeve
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Kitchen GFI's

Hello Bill and Steve, those three posts were on top of each other. :D

Roger
 