The IT wiring is an Article 800 installation. 800.48 requires that any Chapter 3 wiring methods used for this wiring be installed per the appropriate Chapter 3 Article. The Chapter 3 raceway articles do not require that the raceways be grounded. The requirement that raceways be grounded is in Article 250, and since Chapter 8 is a stand alone article, these raceways are not required by the code to be grounded. There may be design issues, as Bennie stated, that would require this raceway to be grounded, but not a code requirement.
Don