Bennie, this is a subject I do not see eye-to-eye with you. No disrespect intended.
Here is my point of view. Lets take any power source and make an isolated ground for it. The power source can be anything like a service entrance, isolation transformer, battery plant, UPS, generator, etc. To make an IG you have to establish a ground window. The ground window is a location (usually a ground bar or Xo) that separates the isolated ground plane from the integrated ground plane. The integrated ground plane is where all the metallic parts form multiple loops, and are multi-grounded to the electrode system like a grid.
Now lets assume we are going to install a 480 VAC 3-phase delta input, 208Y/120 output transformer that we want IG installed on the feeder and branch circuits. We need to bond the output of the transformer to some kind of ground electrode to be code compliant. So for this design we choose to bond the neutral at the first disconnect device. So we run an GEC from the building steel or service ground electrode, makes no difference which by code, to the neutral bus in the disconnect device. We then install a bonding jumper from the neutral bus to ground bus, and install another bonding jumper from the ground bus to an isolated ground bus. By doing this we have installed a ground window inside the disconnect device, and established both an integrated ground plane and isolated ground plane. Now from the disconnect device we can run both EGC?s (integrated ground plane conductor), and IG?s (isolated ground plane conductors) to feeder and branch circuits as needed. This ground window forms the SPG, not the service ground. The service ground is in the integrated ground plane. The isolated ground plane is can be down stream or wherever we want it.
Here is the point. If the power source is SPG to the integrated ground plane, then it does not matter what common mode currents are flowing or what voltages are developed. The grounded conductor has a single bonding point to the electrode. All the noise in the integrated ground plane is reference to the grounded conductor at the single point. Therefore the ungrounded conductors are in phase and in common mode reference with the noise. If you were to take an oscilloscope and reference its ground to the IG buss then look at the grounded conductor and ungrounded conductors you would not see any noise, it?s irrelevant. Now as long as you do not corrupt the IG circuit downstream via multi-ground, you cannot inject any common mode noise or current other than brute force EMF/RFI.
This is the basic principle used in most telephone switching offices and radio transmission sites. Even equipment manufactured for home use like HAM radio gear and PC?s use this principle. It?s the DC power supply built into them that make the SPG via the step down transformer supplying the DC rectifiers. It?s the power source that forms the SPG not necessarily the service entrance.