Originally posted by sparky46514:
Can you give me the code section that prohibits this Tom? I also think that this is moot as we used greenfield to pipe to box. Thank you for the info though. AJ
I believe that 250.119 of the 2002 NEC requires that Equipment Grounding Conductors (EGCs) that are #6 AWG or smaller "shall have a continuous outer finish that is either green or green with one or more yellow stripes except as permitted in this section." I cannot see how subsection B would apply in most installations short of industrial environments were an electrical maintenance staff is employed.
250.119 Identification of Equipment Grounding Conductors.
Unless required elsewhere in this Code, equipment grounding conductors shall be permitted to be bare, covered, or insulated. Individually covered or insulated equipment grounding conductors shall have a continuous outer finish that is either green or green with one or more yellow stripes except as permitted in this section.
(A) Conductors Larger Than 6 AWG. An insulated or covered conductor larger than 6 AWG copper or aluminum shall be permitted, at the time of installation, to be permanently identified as an equipment grounding conductor at each end and at every point where the conductor is accessible. Identification shall encircle the conductor and shall be accomplished by one of the following:
(1) Stripping the insulation or covering from the entire exposed length
(2) Coloring the exposed insulation or covering green
(3) Marking the exposed insulation or covering with green tape or green adhesive labels
(B) Multiconductor Cable. Where the conditions of maintenance and supervision ensure that only qualified persons service the installation, one or more insulated conductors in a multiconductor cable, at the time of installation, shall be permitted to be permanently identified as equipment grounding conductors at each end and at every point where the conductors are accessible by one of the following means:
(1) Stripping the insulation from the entire exposed length
(2) Coloring the exposed insulation green
(3) Marking the exposed insulation with green tape or green adhesive labels
(C) Flexible Cord. An uninsulated equipment grounding conductor shall be permitted, but, if individually covered, the covering shall have a continuous outer finish that is either green or green with one or more yellow stripes.
--
Tom