Is Bonding Bushing on Rigid Stub Up Required

Status
Not open for further replies.

ed downey

Senior Member
Location
Missouri
I have parallel feeders that stub up into an Open Bottom Switchboard.

The Installation is PVC Schedule 40 to a Fiberglass 90 then a piece of Rigid Steel Conduit riser (Approximately 2' to 4' in length) to above the concrete slab into the bottom of an open switchboard.

The way I read 2014 NEC 250.86 Exception #2 is that I do not need to install a Bonding bushing on the rigid stub ups because they are Short Sections of Metal Enclosure to provide Support or protection.

Let me know your thoughts.

Thanks Ed
 

ed downey

Senior Member
Location
Missouri
Thanks after seeing your post I went and re-read the exception and it is clearly indicating that it only applies to cables.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Since your metal RMC is actually part of the raceway system it requires bonding. What's curious about this section is say that you ran your PVC through a short section of RMC would that RMC need to be bonded?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Since your metal RMC is actually part of the raceway system it requires bonding. What's curious about this section is say that you ran your PVC through a short section of RMC would that RMC need to be bonded?
It would seem not according to the wording.
 