Recently an inspector required the 120 volt circuit to a intrinsically safe relay, to be GFCI protected. He said because the relay isn't UL listed. Can anyone explain this resoning. Thanks for the help.
 

tom baker

First Chief Moderator
Staff member
Re: Intrinsically safe relays

Possibly may be a requirement in the UL listing for IS systems, there is a UL standard 1394 or similar. Use of a GFCI is allowed in UL 508 Industrial Motor Control Standard for non listed equipment.
 