tiger4life
Member
- Location
- Alabama
- Occupation
- Business Manager Electrical Construction/Master Electrician
I have a project were we will installing ATS on shelters and need some help. These shelters are supplied by service on pole with meter + fused disconnect then it runs to another fused disconnect on shelter that is back to back with MB panel inside. Last year when mounting ATS we simply removed disconnect on shelter and replaced it with a "service entrance rated" ATS. This year they want to leave disconnect and install ATS in between them which creates a big headache.
My question is if I mount ATS beside or close by disconnect and install large enough conduit can I run conductors from load side of disconnect to ATS and load conductors from ATS through same conduit and through disconnect to inside shelter using existing nipple between wall.
http://s7.photobucket.com/user/tiger4life/media/Document1pdf.jpg.html
My question is if I mount ATS beside or close by disconnect and install large enough conduit can I run conductors from load side of disconnect to ATS and load conductors from ATS through same conduit and through disconnect to inside shelter using existing nipple between wall.