Informing owner of using copper clad aluminum

Status
Not open for further replies.

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
I would think it would need to dual rated. Time to read some more.
First thought off the top of my head. if in Al column column for ampacity would be considered Al/ cu.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
Device I can see since it copper on the outside of the conductor. Would a wire nut spring cut through the cu coating and come in contact with the Al.
I will look up wire nut bands and see if compatible.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
I'm reading 110.14 2014 NEC.
Will see if any change in 2017.
I do not have a 2020 to see if change is made.
The way I read it the wire nut in this case would need to be "identified for purpose and condition of use". For copper to copper clad.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I'm reading 110.14 2014 NEC.
Will see if any change in 2017.
I do not have a 2020 to see if change is made.
The way I read it the wire nut in this case would need to be "identified for purpose and condition of use". For copper to copper clad.
I'd have to research it, but I think all wire nuts are so listed.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
One of the proponents arguments for copper clad AL is that you can use standard devices, wire nuts, etc.
Yes, first I was going to say that of course you can use any copper device/termination with CCAL, as the contact surfaces are copper. But then I started to wonder whether the connection design has to take into account the thermal expansion coefficient, as presumably for CCAL that's closer to Al than Cu, and they differ (ratio of 23/16).

Cheers, Wayne
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The issue with the early small aluminum wires was thermal expansion and contraction, not surface conductivity.

Does the copper cladding reduce expansion by constricting the aluminum, or will it ooze out of the cut ends?

Added: Wayne, GMTA. :giggle:
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
The one we use the most say cu to cu only.
So your opinion would be that the cu to cu would cover the use of copper clad to copper clad.
Interesting, thank you.
I also was looking at box fill using #10 copper clad. I can see some installation practices need to be adjusted.
I also see where 314.16 (B) (4) can gain an advantage on box fill if a cu to cu wire nut can be used.
That may make a good test question.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
On the wire nut question. I did find this. I would say Texie was right. According to what I read from NEMA there should be a change in wording of 110-14.
May be time to buy a new book.
 

Attachments

  • Screenshot_20220509-210222.png
    Screenshot_20220509-210222.png
    399.5 KB · Views: 26

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Good point. It'd be fun stuffing a box with two #10 cables and a GFCI. :confused:
Yes, box fill is already an issue with many ill informed electricians. There will need to be an adjustment in the everyday electricians thinking if CCA is going to be a thing as I suspect it will.
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
So I have access to copper clad nmb.
Have not used much but what little I have I liked.
I want to wire a house in this. Would you inform owner. Or not worry.
I don’t think it’s is an issue, though I might be thinking with my pocket book.
I think...
Thinking with your pocketbook about materials can really cost a lot of time, which is more expensive.

Same thing I suggested on your shop.
Materials, even expensive materials, are cheaper than labor

I don't know how big of a house you're looking at, but my last one was about 2600 sf

I used 2250 ft of 14/2 ($1,480), 750 ft of 14/3 ($510) and 1000 ft of 12/2 ($720)

Looks like $2710

If you save 30% on wire, that's about $800

How much time will it burn to save $800 ?

Considering the larger wires, more box fill, etc you may have to rethink and reroute lighting circuits. I would imagine your #10 CCAL will take longer when making up receptacles - pigtailing #10 grounds could be a chore

and most assuredly take longer installing devices on the finish.

Are your Romex connectors at the panel rated for (2) 10/2 cables? That would suck to run out of KOs and have to bring some in from the bottom. It would take more length of your cheaper wire, cutting into your savings.

For me, it's just not worth it.
Time burner at its worst.

And that will cost more than the $800 in wire savings
 