Working on a school where Air Conditioning is being added.
I did the calcs per 220 for a school and the service is large enough just have to let Power Company know of the additional load since their transformers are feeding the building.
AC is being done by a VRF (Variable Refrigerant Flow) heat pump system and some new RTU's. The total AC load with all condensing units and RTU's is about 800A. However there is also 80KW worth of electric duct heaters which will reheat the cooled air if a thermostat in a certain area is turned up so it will kick in the duct heater and heat up the already cooled air to help deliver air that is a bit warmer to the space. (used a lot commercially but not very efficient if you ask me)
As I am designing the panels required for the new AC loads I want to also use these panels to power up the new electric duct heaters. So typically you size the panels for the larger of the 2 loads Heat or AC. But in this case the duct heaters are designed to be used during the summer months. Is there a demand the NEC would allow in this situation. I know about the 65% for heat pump auxiliary heat in the optional calculations but that is for a dwelling unit, this is a school. I hate to have to add in the full load of the 80KW of electric heat knowing there is no way all 80KW will be in use the same time the AC is running. Its 'bad' enough I am required to use 100% of the AC load knowing there will be some demand factor and all 22 Condensing units and 4 RTU's will not run at the same time, I accept that as part of the NEC's requirement for AC load.
Can anyone offer anything in the NEC that tells me I do not have to include 100% of the duct heaters as well? I went through Article 220 twice.
I am in PA, we are NEC 2014
Thanks you!
I did the calcs per 220 for a school and the service is large enough just have to let Power Company know of the additional load since their transformers are feeding the building.
AC is being done by a VRF (Variable Refrigerant Flow) heat pump system and some new RTU's. The total AC load with all condensing units and RTU's is about 800A. However there is also 80KW worth of electric duct heaters which will reheat the cooled air if a thermostat in a certain area is turned up so it will kick in the duct heater and heat up the already cooled air to help deliver air that is a bit warmer to the space. (used a lot commercially but not very efficient if you ask me)
As I am designing the panels required for the new AC loads I want to also use these panels to power up the new electric duct heaters. So typically you size the panels for the larger of the 2 loads Heat or AC. But in this case the duct heaters are designed to be used during the summer months. Is there a demand the NEC would allow in this situation. I know about the 65% for heat pump auxiliary heat in the optional calculations but that is for a dwelling unit, this is a school. I hate to have to add in the full load of the 80KW of electric heat knowing there is no way all 80KW will be in use the same time the AC is running. Its 'bad' enough I am required to use 100% of the AC load knowing there will be some demand factor and all 22 Condensing units and 4 RTU's will not run at the same time, I accept that as part of the NEC's requirement for AC load.
Can anyone offer anything in the NEC that tells me I do not have to include 100% of the duct heaters as well? I went through Article 220 twice.
I am in PA, we are NEC 2014
Thanks you!