I need a reference citation on wire voltage ratings.

Status
Not open for further replies.

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I've noted some threads regarding ungrounded/high-resistance grounded systems.

I no longer have access to the ICEA standards, but the definition of voltage-rating with respect to conductors is slightly different than with general equipment and it affects the proper use of the these systems if a ground-fault is not cleared in a timely manner.

I believe the definition is effectively based on the three-phase voltage of the system, but I can't find a clear reference in either the UL or NEMA documents I have available.

Essentially, the question is: When I say I have 600 Volt rated wire, what does the 600V refer to? And from what Standard is it cited?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Re: I need a reference citation on wire voltage ratings.

Thanks, that is the system and transmission/distribution equipment standard. Wire is rated differently.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Re: I need a reference citation on wire voltage ratings.

I now know the standard I'm looking for: ANSI/NEMA WC 70-1999/ICEA S-95-658-1999.

If anyone has access to it please PM me. I only need a short reference.
 