hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
So I have 7 vavs fed from on branch circuit #1.
Vav-1: MCA: 0.28A, MOCP: 15A
Vav-2: MCA: 0.28A, MOCP: 15A
Vav-3: MCA: 0.28A, MOCP: 15A
Vav-4: MCA: 0.28A, MOCP: 15A
Vav-5: MCA: 0.28A, MOCP: 15A
Vav-6: MCA: 0.28A, MOCP: 15A
Vav-7: MCA: 0.28A, MOCP: 15A
My #1 branch circuit breaker size provided is 20A that feeds all 7 vavs above. Cable size provided is #14 awg.
Would the branch circuit #1 breaker size be 15A or 20A?
Vav-1: MCA: 0.28A, MOCP: 15A
Vav-2: MCA: 0.28A, MOCP: 15A
Vav-3: MCA: 0.28A, MOCP: 15A
Vav-4: MCA: 0.28A, MOCP: 15A
Vav-5: MCA: 0.28A, MOCP: 15A
Vav-6: MCA: 0.28A, MOCP: 15A
Vav-7: MCA: 0.28A, MOCP: 15A
My #1 branch circuit breaker size provided is 20A that feeds all 7 vavs above. Cable size provided is #14 awg.
Would the branch circuit #1 breaker size be 15A or 20A?