HVAC equipment circuit

Status
Not open for further replies.

mannyb

Senior Member
Location
Florida
Occupation
Electrician
The 120v circuit near air handler and or controls in attic. Does that circuit need to be dedicated for that equipment ONLY? If so can could someone help me with nec reference. I had customer tell me HVAC guys wouldnt work on hvaC because it was being used for lighting in attic and it had to be dedicated for warranty
 

Eddie702

Licensed Electrician
Location
Western Massachusetts
Occupation
Electrician
I would say the AHU needs to be on a dedicated circuit. 422.12 Central Heating Equipment requires a dedicated circuit. Only a pump,valve, humidifier etc related equipment can be connected to the Ahu circuit
 