Superintendant needs a little clarity here from Electrical side ...
Situation : Seeing a 35 amp rated AC condenser with a # 10 conductor . Occasionally seeing #10 on a 40 amp breaker. Sub says NEC provisions allow for this excess for start up draw.
Question 1:
When HVAC condensing units have a maximum breaker rating of 35 amps stamped on the unit..
can the breaker exceed the conductor rating.. if so by how much ? Isn't the # 10 only good for the 30 amp ?
Question 2:
Where can I find the applicable code in the NEC 02' handbook that provides this.
Final Question:
Where can I find reference to maximum length on "Liquidtight" whips ( from disconnnect to unit ) serving condensers. Locally, muni's have been enforcing 6' max. They are running about 12' Is this accurate ?