Thanks for the pleasing replies guys! (Pierre and "1793").
Glad the drawings were of help.
As far as the ratings for the Isolated Transformers goes, the Secondary Voltage may be either 12/24 VAC or 16/32 VAC.
If the choice of Input Voltage to the Motor is in the 230 VAC range, the 12/24 VAC Secondary Voltage type Transformer(s) may be used.
With the Secondary Windings connected in series (as shown in the 1? drawings), an input of 208 VAC will yield an output of apx. 232 VAC.
If the choice is more in the 240 VAC range, go for the 16/32 VAC Secondary Voltage type Transformer(s).
Again, the Secondary Windings are connected in series - like the 1? drawings show; and with an input of 208 VAC, the output will be apx. 240 VAC.
As to the arrangement and KVA Size of the Transformers, I am unsure if this Motor is Single Phase or 3 Phase.
If The Motor Is Single Phase:
Use one Transformer - connected as described in the "Single Phase Voltage Boosting Transformer Setup" drawing. (Primary Windings connected in series adding, Secondary Windings connected in series adding).
For an output of apx. 232 Volts, use a Transformer with these ratings:
* Primary Voltage: 120/240 VAC
* Secondary Voltage: 12/24 VAC
* Minimum Volt-Amps Rating: 500 VA (0.5 KVA)
This will be sufficient for a load Current value of 20.83 Amps maximum, which equates to around 4,832 Volt-Amps (4.8 KVA).
------------------------------------------------------------------------------------------------------
------------------------------------------------------------------------------------------------------
For an output of apx. 240 Volts, use a Transformer with these ratings:
* Primary Voltage: 120/240 VAC
* Secondary Voltage: 16/32 VAC
* Minimum Volt-Amps Rating: 750 VA (0.75 KVA)
This will be sufficient for a load Current value of 23.40 Amps maximum, which equates to around 5,616 Volt-Amps (5.6 KVA).
-------------------------------------------------------------------------------------------------------
-------------------------------------------------------------------------------------------------------
These ratings should be sufficient for a 230 VAC 1? 2.0 HP Motor (FLA = 12.0 Amps), or a 3.0 HP 1? 230 VAC Motor (FLA = 17.0 Amps).
If The Motor Is Three Phase:
Use two Transformers - connected in an Open Delta configuration, as described in the "Three Phase Open Delta Voltage Boosting Transformer Setup" drawing. (Primary Windings connected in series adding, Secondary Windings connected in series adding).
For an output of apx. 232 Volts, use 2 Transformers with these ratings:
* Primary Voltage: 120/240 VAC
* Secondary Voltage: 12/24 VAC
* Minimum Volt-Amps Rating: 500 VA (0.5 KVA)
This will be sufficient for a load Current value of 20.83 Amps maximum, which equates to around 8,369 Volt-Amps (8.35 KVA).
------------------------------------------------------------------------------------------------------
------------------------------------------------------------------------------------------------------
For an output of apx. 240 Volts, use 2 Transformers with these ratings:
* Primary Voltage: 120/240 VAC
* Secondary Voltage: 16/32 VAC
* Minimum Volt-Amps Rating: 750 VA (0.75 KVA)
This will be sufficient for a load Current value of 23.40 Amps maximum, which equates to around 9,727 Volt-Amps (9.7 KVA).
-------------------------------------------------------------------------------------------------------
-------------------------------------------------------------------------------------------------------
These ratings should be sufficient for a 230 VAC 3? 5.0 HP Motor (FLA = 15.2 Amps).
Good luck!
Let us know what the outcome is
Don't let the Smoke out of the Motor or Transformers!
:lol: :wink:
Scott35