Hey guys,
A friend of mine purchased a hot tub for his house and asked if I could assist in the electrical installation. To be honest my background is not in resiential but in industrial and controls.
I am going to be running 6/3 NM Cable from his main panel in an unfinished basement to an outside 50A Spa Panel. To bring the NM cable outside to the Spa Panel I am going to run it in Schedule 80 PVC roughly 2 feet before it leaves the house to the Spa Panel, and from the Spa Panel to the hot tub. My question is what is the insulation type on the conductors for the NM cable so I can size the PVC accordingly to Chapter 9 Tables 4 and 5?
Thanks
A friend of mine purchased a hot tub for his house and asked if I could assist in the electrical installation. To be honest my background is not in resiential but in industrial and controls.
I am going to be running 6/3 NM Cable from his main panel in an unfinished basement to an outside 50A Spa Panel. To bring the NM cable outside to the Spa Panel I am going to run it in Schedule 80 PVC roughly 2 feet before it leaves the house to the Spa Panel, and from the Spa Panel to the hot tub. My question is what is the insulation type on the conductors for the NM cable so I can size the PVC accordingly to Chapter 9 Tables 4 and 5?