680.13 says the hot tub disconnect must be at least 5' away from the inside wall of the tub and be readily accessible and within site of. So is there a max distance? Or is it up to the inspector as far as what he feels is readily accessible and within site of?
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
In-sight from means within sight & not more than 50' away.

IMO, if is around the corner it is not within sight
 