HMCP as feeder

Status
Not open for further replies.

Patil

Member
Location
Canada
Occupation
Electrical Engineer
a777c76442c3c78e45369efeeaea1c56.jpg

Can I use HMCP as a feeder.
Also I’m looking for cable size calculation for the branch.


Sent from my iPhone using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
You can use an HMCP as the short circuit protection for a motor circuit if it is part of a listed combination starter.

Conductor ampacity is determined according to article 430 just like any other motor circuit.

At least in the US. No idea what rules they have in Canada.
 