Heating and AC loads in the optional dwelling load method

Status
Not open for further replies.
I am trying to VE some apartment panels by downsizing them through the optional method. It has been awhile since I've done a dwelling load calculation bear with me. The apartment has a 2.4KVA condensing unit outside and a 7.5KW AHU inside. My question is when I get to 220.82(c) can I only use the AHU under (C)(2) or do I have to use them combined under (C)(1) since the AHU does have cooling capacity?
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Use (C3). 100% of the 2.4kw and 65% of the 7.5kw; the 7.5kw rating should be the supplementary heat strips within the AHU.

So that would be 7.3kw.


Sent from my iPhone using Tapatalk
 

Romel

Member
Location
Florida
Occupation
Designer
Use (C3). 100% of the 2.4kw and 65% of the 7.5kw; the 7.5kw rating should be the supplementary heat strips within the AHU.

So that would be 7.3kw.


Sent from my iPhone using Tapatalk

Isn't Article 220.82 (C)(2) to (C)(3) pertains to heating loads? Whenever I do AC Load Calcs using the optional method, I always go for (C)(1).

If you have a separate space heating/heat pumps, you use 220.82(C)(2) to (3), whichever has a higher demand between (C)(1) and (C)(2) to (6), use that.
The reason being with the option between the cooling demand and heating demand is that heating and cooling wont be used at the same time.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Isn't Article 220.82 (C)(2) to (C)(3) pertains to heating loads? Whenever I do AC Load Calcs using the optional method, I always go for (C)(1).

If you have a separate space heating/heat pumps, you use 220.82(C)(2) to (3), whichever has a higher demand between (C)(1) and (C)(2) to (6), use that.
The reason being with the option between the cooling demand and heating demand is that heating and cooling wont be used at the same time.

Setup described by OP is a split system with condensing unit and AHU.

The condensing unit is used for heating and cooling, as it pulls and dumps heat.

The 7.5kw rating they gave is for the auxiliary heat strips in the AHU, so if emergency heat is being used, both the condenser and heat strips are typically active unless the system is setup to lock out the condensing unit.


Sent from my iPhone using Tapatalk
 

Romel

Member
Location
Florida
Occupation
Designer
Setup described by OP is a split system with condensing unit and AHU.

The condensing unit is used for heating and cooling, as it pulls and dumps heat.

The 7.5kw rating they gave is for the auxiliary heat strips in the AHU, so if emergency heat is being used, both the condenser and heat strips are typically active unless the system is setup to lock out the condensing unit.


Sent from my iPhone using Tapatalk

Oh I see, If that's the case the procedure would still be calculate the cooling load per (C)(2), then calculate the heating load using (C)(3) (100% of CU + 65% of the AHU Heat strips if both eqpt is meant to be operating simultaneuously)
Whichever higher should be used for the HVAC Demand :)
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Oh I see, If that's the case the procedure would still be calculate the cooling load per (C)(2), then calculate the heating load using (C)(3) (100% of CU + 65% of the AHU Heat strips if both eqpt is meant to be operating simultaneuously)
Whichever higher should be used for the HVAC Demand :)

No, you would only use (C)(3). (C)(2) is if there is no supplemental heating and has nothing to do with cooling; with a split system, you do have supplemental heating. The compressor is the primary means of heat but you still have auxiliary strips within the AHU.

Maybe I can explain better;

(C)(1) is for air conditioning only
(C)(2) is for heating only without supplemental heat
(C)(3) is for heating with supplemental heat

pick the larger of those three, unless 4,5,6 would apply to your install. (C)(3) is the setup described by OP and is guaranteed to be the largest load of 1, 2, & 3.
 

Romel

Member
Location
Florida
Occupation
Designer
Oh I see, If that's the case the procedure would still be calculate the cooling load per (C)(2), then calculate the heating load using (C)(3) (100% of CU + 65% of the AHU Heat strips if both eqpt is meant to be operating simultaneuously)
Whichever higher should be used for the HVAC Demand :)
"...still be calculate the cooling load per (C)(1)" (correction)

and yes I think we are on the same boat brantmacga. :)
 

frofro19

Senior Member
Location
VA.
Occupation
Master Electrician
No, you would only use (C)(3). (C)(2) is if there is no supplemental heating and has nothing to do with cooling; with a split system, you do have supplemental heating. The compressor is the primary means of heat but you still have auxiliary strips within the AHU.

Maybe I can explain better;

(C)(1) is for air conditioning only
(C)(2) is for heating only without supplemental heat
(C)(3) is for heating with supplemental heat

pick the larger of those three, unless 4,5,6 would apply to your install. (C)(3) is the setup described by OP and is guaranteed to be the largest load of 1, 2, & 3.
Where does mini-split systems fit in?
 