can you use aluminum lbs in a class 2 div 2 area must the connectors be listed for the liquid tight and is the liquid tight listed it self
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
can you use aluminum lbs in a class 2 div 2 area must the connectors be listed for the liquid tight and is the liquid tight listed it self

If the LB's are listed for Class II Div 2, then they are listed, period, regardless if they are aluminum or cast iron. Likewise the connectors, and having one listing does not imply having the other.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Oddly enough, Aluminum RMC and associated fittings (Article 344) are not specifically listed for any classified location. They are, however, approved for Class II, Division 2 under Sections 344.10 (A)(3) and 502.10 (B)(1) & (2). Aluminum LBs must be consistent with Section 502.10(B)(4).

Section 344.6 simply requires LBs to be listed although not specifically for Class II, Division 2.

"LFMC" that is not listed is not LFMC. [See Section 350.6]
 