grounding two services

Status
Not open for further replies.

voltage37

Member
Location
Indiana
If you have two services of different voltages located on the same building side by side do you use the same grounds for both services? Or do you drive ground rods for each service and ground them separate. I think you use the same ground rods for both services.
 

bphgravity

Senior Member
Location
Florida
Re: grounding two services

Section 250.58 requires a common grounding electrode system when two services supply the same building.
 