Grounding telephone service entrance

Status
Not open for further replies.

hydrobob

New member
I have a client with an older house. Both the power and the telephone services (point of connection to the utility) were originally on a pole several hundred feet from the house. Several years ago they had a second phone line installed and the phone company moved their interface box from the pole to the house. The new telephone interface box is not grounded to anything. Since then they have had repeated damage to telephone equipment due to lightning. All the equipment damaged was connected to both the telephone and the power systems. They asked the telephone company to check out the problem and the telephone company agreed that the interface box should be grounded and wants to ground it to the neutral in the main power panel in the house. Is this a good idea? Any other suggestions?
 

bennie

Esteemed Member
Re: Grounding telephone service entrance

Don't ground at the neutral. Ground where the neutral is grounded.
 

tom baker

First Chief Moderator
Staff member
Re: Grounding telephone service entrance

Bennie is correct. The bonding point for all the telecommunications should be at the service grounding point, to minimize the potential difference between the systems in a lighting strike or overvoltage. bonding at different points as it is now, creates a potential, due to voltage drop, when causes a current flow, damaging equipment. Also a TVSS for the house and telecommunications gear should be installed at the service entrance.
 

bennie

Esteemed Member
Re: Grounding telephone service entrance

Tom: Much better ;) I learned a new term for common mode voltage and current. I read it in a book authored by O.C.Seevers, PE.

NE voltage, and NE current. NE (Neutral Earth).

I like that term and will use it instead of common mode.
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Grounding telephone service entrance

It is obvious why you have had problems. As already stated the NID needs to be bonded to the service electrode.

Do not bond the NID to a seperate electrode as some Telco's would do as this will only amplify the probelm. If a seperate electrode is selected it must be bonded to the service electrode to be effective.
 

shlcmid

Member
Re: Grounding telephone service entrance

What do you do when you have a meter on a pole some 60 feet overhead from the house with only a three wire entrance into the house? Telco is on the other side of the house (satellite and aerial are also on another side!). I am suggesting a ground ring but how effective will that be since this house has such a long run of electric service line without any additional grounding (meter pole would be closest ground except the telco separate ground on other side).
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: Grounding telephone service entrance

shlcmid: You have gotten me thinking about the possibility that my own home might have a grounding issue. But I?ll start a new thread, rather than diverting this one.
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: Grounding telephone service entrance

shlcmid,

You could run a 10AWG copper wire from the telco entrance around the outside of your house and connect it to your ground rod.

Dave
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Grounding telephone service entrance

If the distance from the telephone system primary protector is over 20'from the service grounding system, then the exception to 800.40(A)(4) requires a communication system grounding electrode per 800.40(B)(2)(2) and a #6 copper bond from the commnications electrode to the service electrode. Note that this section only applies to one and two family dwelling units.
Don
 

brian john

Senior Member
Location
Leesburg, VA
Re: Grounding telephone service entrance

Bennie:
I know you have issues with some of the NEC grounding practices and your allowed that's what keeps thing moving. My issue has always been terminology.

Pick 4 licensed electricians and ask them the difference between a GEC and an EGC and the grounded conductor and a neutral conductor. See how many can answer the question, in my expierence few could.
 

bennie

Esteemed Member
Re: Grounding telephone service entrance

Brian: I have no problem with GEC and EGC as identification terms.

My problem is the use of words that indicate what a conductor has done, will do, and might do.

Specifically the old "ed" and "ing" use.
Ask fourty electricians, "which one is the ground, grounded, and grounding conductor"? find out how many get it correct.

Actually... find out how many care :D

[ June 30, 2003, 10:25 AM: Message edited by: bennie ]
 