Grounding of double runs power cables

Status
Not open for further replies.

Iphonest

Member
Location
KSA
Occupation
Electrical Engineer
Hi,

We have a big warehouse (20,000 Sq meter) where government electricity is split into 4 different feeders in 4 different locations, To provide electricity to the warehouse we have 4 MDB for each feeder.

The connection between feeder and MDB will be double runs in parallel of 600 MCM [2(4Cx300mm^2)]. and a ground cable of 300 MCM (1Cx150mm^2).

Now my question is DO we have to use 2 runs of ground cable or one ground cable is enough?
 
Last edited:

tom baker

First Chief Moderator
Staff member
Does your location use the NEC?
Are your parallel runs in one racewsy or two?
Under the NEC, each raceway requires a full size EGC.
The size is based on table 250.122
 

Iphonest

Member
Location
KSA
Occupation
Electrical Engineer
Does your location use the NEC? No
Are your parallel runs in one racewsy or two? One cable tray.
Under the NEC, each raceway requires a full size EGC.
The size is based on table 250.122

Thank you for your reply
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If you're using cables or other assemblies, each one should have an EGC sized as if it was the only one.

If you have just a bundle of individual conductors, then one correctly-sized EGC is all you need.
 