Grounding new structure

Status
Not open for further replies.

Patil

Member
Location
Canada
Occupation
Electrical Engineer
We are installing new Surface Condenser and want to know if I have to consider grounding the structure.It’s isolated from the existing building.

Or Can the structure itself will act as ground.
Please suggested there is grounding to be done, pls suggest the calculations and considerations.
Thanks


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If the "Surface Condenser" is a piece of equipment then the equipment grounding conductor with the circuit conductors provides the only required "ground" per the NEC definition of a structure:
Structure. That which is built or constructed, other than equipment
 

kwired

Electron manager
Location
NE Nebraska
If the "Surface Condenser" is a piece of equipment then the equipment grounding conductor with the circuit conductors provides the only required "ground" per the NEC definition of a structure:
Structure. That which is built or constructed, other than equipment
Also a structure supplied by a single branch circuit doesn't need a GEC either. Not sure about in Canada though.
 