I am installing a 5 gang meter socket that will feed 3 100 amp panels for 3 apartments, a 100 amp panel for a commercial rental area and a 200 amp panel for a second commercial rental area. I want to run a 1/o awg copper to the water bond and tap off this to each disconnect with #6awg copper for each 100 amp disconnect and a #4awg copper for the 200 amp per 250.30(A)(3).
My question is: Is there a way to connect the taps with out a crimp or weld? Does a split bolt with tape on it meet the requirment of an irreversible compression connector? Can I also bring just one #6 awg copper conductor from the ground rods to the first main disconnect outside the building instead of bringing a conductor from each disconnect to the ground rods?(All 5 main disconnects are ganged together and bonded together.)
My question is: Is there a way to connect the taps with out a crimp or weld? Does a split bolt with tape on it meet the requirment of an irreversible compression connector? Can I also bring just one #6 awg copper conductor from the ground rods to the first main disconnect outside the building instead of bringing a conductor from each disconnect to the ground rods?(All 5 main disconnects are ganged together and bonded together.)