grounding a seperatly derived system

Status
Not open for further replies.

Willie P

New member
When grounding a transformer, you have a equipment grounding conductor from the panel feeding the x-former. And if you go from the case to building steel for your GEC. Then, from XO to the case for the SBJ. On the secondary side, you come off of XO to your panel for your nuetral. What is the grounding conductor you take to the panel? Is it a EGC or a EBJ? And how is it sized?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Re: grounding a seperatly derived system

250.30 Grounding Separately Derived Alternating-Current Systems
(A) Grounded Systems ..................................................

(1) System Bonding Jumper An unspliced system bonding jumper in compliance with 250.28(A) through (D) that is sized based on the derived phase conductors shall be used to connect the equipment grounding conductors of the separately derived system to the grounded conductor.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: grounding a seperatly derived system

As Augie said you need to size the conductor according to the size of the derived or in this case secondary conductors. This means you would use the table 250.66.
 