You really think that will get through the 2008 code making process? As one of the submitters of that concept for the 2005 code, I would like to see it, but after the exposure in the 2005 code making process, I expect very heavy resistance to the concept. I think that is a change that has long been needed and will help many under stand the concepts. Almost everything that we now call grounding is really bonding.Midget, I am not intending to make this more confusing but the 2008 NEC will change the term grounding conductor to bonding conductor in most places.
It just doesn't work that way. The grounding connection to earth can never provide a "zero volt to ground (earth) potential under fault conditions. Under fault conditions, everything connected to the grounding and bonding system will have a voltage to earth equal to the voltage drop of the part of the fault return path betweeen the main bonding jumper and the power source.... so that all metallic points at any location in a system or installation that could introduce a shock-hazard have a Zero-voltage-to-Ground potential ...
Statements like this are one of the main reasons the change in wording is required. "Ground fault" currents are not trying to get to ground (earth), they are trying to get back to the power source. We do not need a connection to earth to clear building system faults.... and that all such points will have a low-impedance path-to-Ground for conducting Ground-Fault currents.
Would that be similar to how when the utility guys want to bare-hand lines they can like hook on to it, and be at the same voltage? I probably didn't explain that right...lolOriginally posted by roger:
Don, I hope Charlie is right and your proposal goes through for 2008.
I would also like to add (I know that most here know this but for Midget) that bonding does not have to mean zero potential to any other surface, but rather equal potential, even if this is 12,120,277 v (not necessarily desired though ) or what have you.
If we, or equipment, are at this same potential with protection from being between a surface of another potential, all is well.
Roger