catchtwentytwo said:
SCRs are Silicon Controlled Rectifiers
(applications include) Duct Heaters.
(For cl/amp Hz function) See Fluke Application Note:
Troubleshooting Power Harmonics The whole article shows ways to detect the presence of harmonics without elaborate PQ analyzers.
Thank you for brining this to the table. That Fluke PQ guide was an excellent read for me, which answered some long overdue questions.
The 800# in that article got Fluke tech.support, which explained Fluke's 337 cl/amp meter Hz function. This detects the largest magnitude Hz only. That means it only shows 50/60Hz fundamentals on phases, not harmonics, so clamp Hz diagnostics is limited to the neutral.
Efforts to find
a poor mans harmonic detector on shared neutrals may confirm harmonics, but won't trace the source to specific loads. Neutral indicators also suffer the
limits of common mode voltage (last part).
Measuring a shared neutral @ 50/60Hz would confirm an unbalance, and Fluke support said the 337 clamp measures neutral harmonics if zero-sequence sums are the predominate magnitude (ie) 180Hz. At this writing, the 337 retails for U$D 340.00. Fluke's 175, 177, 179 meters (similar Hz function) with the seperate I400 clamp accessory, retail for about the same.
Fluke support confirms tracing phase harmonics directly require PQ analyzers, currently their cl/amp LH1060 is U$D 749.00 or 2060 U$D 1095.00. Nevertheless that
Fluke PQ guide suggested another technique with a much simpler True-RMS cl/amp.
While Flukes PQ guide describes using special peak measurements as well, if the poor mans PQ meter exists, its simplest form may be comparing the phase current against the load or kVA nameplate (E*I). Excluding other variables, if the RMS current of phase(s) exceed its load nameplate or xfmr nameplate, harmonics may be assumed. Fluke's lowest end True-RMS clamp is that I400 attachment, (400A Max) @ U$D 100.00