gounded conductor in XFMR primary

Status
Not open for further replies.

jimioy

Member
In one of our many facilities I found a pad mount 12,470V delta/480V Y feeding a 480V delta/208/120V Y XRMR. There was a neutral between the two XFMRs. Should it have been left out, since the SDS 208/120V secondary derived a neutral?
 
jimioy said:
In one of our many facilities I found a pad mount 12,470V delta/480V Y feeding a 480V delta/208/120V Y XRMR. There was a neutral between the two XFMRs. Should it have been left out, since the SDS 208/120V secondary derived a neutral?


Was the neutral conductor terminated?

It is not required to be installed. I am not even sure where a Wye secondary supply to a Delta primary tranformer would have a primary neutral terminated.
 

cpal

Senior Member
Location
MA
jimioy said:
In one of our many facilities I found a pad mount 12,470V delta/480V Y feeding a 480V delta/208/120V Y XRMR. There was a neutral between the two XFMRs. Should it have been left out, since the SDS 208/120V secondary derived a neutral?


maybe it was the EGC and it looked like it originated at the XO????
 