GEC size when adding a new meter for an ADU

Status
Not open for further replies.

Bpscan

New User
Location
Hayward, CA
Occupation
Electrician
House has 200amp service with a 4 AWG bare copper GEC connected to a ground rod.
We're adding a new dwelling unit in the backyard with a 125amp service. There'll be one service drop (350kcmil) connecting to a gutter where I splice to the existing meter panel (2/0 copper) and the new meter panel (#2 copper) I've already driven a second ground rod about 8 feet away from the original one. My question is, what size do all the wires connecting to the ground rods need to be? I'm looking at 250.66 and see that I need #2 for 350 amp service? Each individual meter enclosure requires smaller than #2 if I look at them individually, but I know I have to bond the two ground rods together, so is this where the #2 comes into play, in between the rods? Then a #4 up to the existing meter and a #8 up to the new meter? That doesn't seem right to me.

Thanks in advance for the help!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
There are several ways to do this post #2 has one method that's how I would do it. Existing #4 GEC to first rod> #6 bonding jumper to second rod> #6 GEC to new service.
 