GEC passing thru grounding bushing

Status
Not open for further replies.
Why can't the GEC pass thru a grounding bushing before landing on the neutral bar in my service panel? In my MH- understanding the NEC 2020, there is no graphic showing this, only a 2nd conductor from the neutral bar to the grounding bushing (fig 250.51 pg. 248)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Are you asking why can't the GEC connect to the grounding bushing? If so the answer it that it can. It is also permissible to install a separate bonding jumper to the bushing.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How about this:
09-20-code-comments-graphic-S36817_C06-40.jpg


 