GE A-SERIES 120/240 1P-3W as a substitute for 120/208 panel

Status
Not open for further replies.

Romel

Member
Location
Florida
Occupation
Designer
Will there be an issue if I use the GE A-Series 120/240 1Phase-3W panelboard for a 120/208 1Phase Application?
I can't find a GE panelboard that is specific for single phase 120/208V application.
I think it will be fine, what do you think?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
There is no panel specific for 120/208 single phase. You should find that your chosen panel actually says something like Maximum of 120/240V.
 