Hey guys, I have a tiny gas furnace I assume the blower will pull 3-4 amps max and a 7 gallon electric water heater that will pull 12 amps. Can I put them both on the same 20amp circuit? I can't find anything in NEC against it.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Hey guys, I have a tiny gas furnace I assume the blower will pull 3-4 amps max and a 7 gallon electric water heater that will pull 12 amps. Can I put them both on the same 20amp circuit? I can't find anything in NEC against it.

422.10, 422.11, 422.13
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Nope.

422.12 Central Heating Equipment. Central heating equip‐
ment other than fixed electric space-heating equipment shall
be supplied by an individual branch circuit.
 