Where do I find the NEC support requirements for Flexible connection fittings ???????????????????????????????????????????????

Thank you
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
If we are discussing hazardous locations only - Section(s) 501.140(B)(3)&(4). Otherwise, the requirements for "ordinary" locations hold and depend on the applicable wiring method.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
You have set up a chain of requirements beginning with Sections 501.10(A)(2) or (B)(2) with emphasis on the necessity rather than the convenience of a flexible connection. Then Section 300.11 plus the securing/supporting requirements of the rest of the associated wiring method such as RMC or IMC (usually Section 3xx.30) are applied along with Section(s) 501.140(B)(3)&(4). The general emphasis beyond securing/supporting the flexible coupling as part of the overall wiring method is avoiding stress on the connections/terminations.
 