I Know This Probably Isn't The Correct Place To Post This Questions But I Figured I would Give It A Shot.
In What Code (If Any) Does It Require That A Fire Pump Be Monitored For Voltage, Current, Rotation, etc.
I am Not Sure But Possibly In NFPA 72 Or NFPA 101.
Any Help In This Research Would Be Appreciated.
-Ed
 

jmc

Member
Location
Massachusetts
Re: Fire Pump Monitoring

The answer to your questions can be found in NFPA 20 the standard for Fire Pumps. Chapters 6 and 7 provide the requirements for electric fire pump motors and controllers. Section 7-4.6 will answer the question.
regards, John
 