Finish ratings 362:10 (2) I N

Status
Not open for further replies.

Cmc

Member
I had a question on a test today of fire ratings. Q. Equipment for feeder circuits (including transfer switches, transformers, and panel boards) shall be located either in space fully protected by approved automatic fire suppression systems (including sprinklers,carbon dioxide systems) or in a_________ fire resistant rating.
A.15 minute B. one hour C. two hour D. four hour

Finish rating 362:10 (2) I N say A
The answer came in
700:10 D C
My question is why don't they post all fire rating under one Article
 
Last edited:

jumper

Senior Member
Because nothing in the NEC is set up that way.

Think of all the sections that would be associated with installing a receptacle in a resi kitchen counter. 210.52, 314.XX, 210.11, 310.16, 210.8, and so on.
 
Status
Not open for further replies.
Top