fertilizer storage, Class 1, Div 1?

Status
Not open for further replies.

ver

Member
Would you give a hazardous location classification to a building where fertilizer in bags are werehoused? Reasons? If you have any direct experience or stories, that would be helpful too.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Re: fertilizer storage, Class 1, Div 1?

At worst, this is likely to be a Class II, Division 2 location. It is even more likely, with good housekeeping practices, that it would not need to be classified at all. Reference NFPA 499, Section 3-3.1(a).

It is critical to get the MSDS for the product and review the manufacture?s recommendations.

Edit added reference.

[ February 16, 2005, 12:57 PM: Message edited by: rbalex ]
 