I'm doing the calculation for a fitness club. that is in a strip mall.That has the following items.
1. 3200 square ft X 3 = 9600
2. 30 kw heat. =30,000
3.40 receptacles. =7200
4.8- 16amp treadmills =15,840
5. sign requirement =1200
6.show window =4000
7.10 kw water heater =10,000
_______
77,840
77,840 / (240 x 1.732) = 187.25 = 200amp breaker
since this is a gym and not a store, can I subtract out the show window requirments, and if the treadmills are reduced to 12 amp motors
11,880. This would give a new calculation of.
69,480 / (240 x 1.732) = 167.14 = 175amp breaker and the use of 4/0 al
If you see anything I'm missing let me know.